Ali,
Warning! TM when incorrectly set can lead to major damage to the asset.
TM is configured in the rack (protection system), not in System1 (analysis software). One needs the following steps to make the TM active:
- Establish the new trip setting you need. TM is the ratio of the new setpoint to the old setpoint. Max TM is 3.
- Decide when TM starts and stops. These two events must be clearly defined by a traceable parameter/signals.
- Connect the necessary wires to the rack to instruct the rack to start and stop the TM based Step 2.
- Using the 3500 rack configuration software, change the TM setting from the default value of 1 to the new value calculated in Step1.
Important Note: if 3500 rack is standard, TM affects all cards and channels in the rack when it's active. The TM is not configured for a specific parameter (e.g. 1X), channel (e.g. channel 3) or slot (e.g. slot 4). So, if the rack is connected to more than one machine, all will be affected.
I hope this helps a little.
Regards- Ali M. Al-Shurafa